In this post you state "Purpose of the EGC is to carry only fault current providing a fault current return path so the breaker can trip and clear the fault"
View attachment 101492
View attachment 101494
If I say it, nobody listens............................... Here it is, straight from the horses mouth. Look carefully at the pics.
You have to bond ALL metal stuff in a building to provide a path from that metal to the ground rod.........in order for lighting induced voltage on those metal things to find a path to where it wants to go..........EARTH . This applies to enclosures, and the metal structure of the building(it it's a metal building).
Induced voltage wants to go to EARTH.
GROUND FAULTS want to go to the UTILITY. The EGC serves a dual purpose..........it carries induced voltage, and ground fault voltage. A
GEC carries voltage from the final bonded point to the ground rod................it carries lightning induced voltage brought to it by the GEC.
A ground rod should NEVER figure into a conversation about getting shocked by touching a live enclosure (this applies to other comments in preceding posts)
PARALLEL CIRCUITS............... You are, and always will be, a parallel circuit to the utility UNTIL the fault is cleared. Ground rods don't have a thing to do with it.........they don't protect you. Only the breaker makes the enclosure safe to touch, AND ONLY AFTER THE FAULT IS CLEARED. I would venture to say, that if you're leaning on an enclosure at the exact instant a hot wire contacts that enclosure..........you're probably toast. For the time it takes to trip the breaker..........you's part of the circuit.
Standard breakers protect EQUIPMENT, and to a very very limited degree people. If a circuit gets hot, the breaker flips........protecting wires, etc. If a hot contacts an enclosure, the breaker flips. If you touch a live wire, the breaker will not flip. This leads to a conversation about GFCI's.
IMHO.