I can't find a step down 3 phase transformer specs : 250 V 3 phase input - 14 volt 3 phase output - 400 watts give or take / this will feed a rectifier with three diode pairs . maybe too far off topic for this forum , if so guide me to a forum please TIA
 
That's pretty specific. Still, lets get even more specific. Do you need 400W total, or 400W per phase? Roughly, that would be either a 0.5kVA three phase transformer or 1.5kVA. What is the design DC voltage you require?

12/24V secondary is a lot more common. Since you are indicating DC output via a 3-phase bridge, and the DC could be regulated more easily, could you use a 16V secondary with the bridge and a 25A regulator trimmed to 14V? If so, you solution becomes a lot easier.
 
my lack of education on this subject is showing ! not looking for any specific DC out put numbers , I was just saying I don't need big capacity .
Maybe this next question will simplify things . I can salvage ( from a HVAC friend ) 3 singlephase transformers - 230 v primary & 24 v secondary ; if I interconnect them in Y or delta will that produce 3 phase or do they have to have a common laminated core ? TIA again
 
if I interconnect them in Y or delta will that produce 3 phase or do they have to have a common laminated core ? TIA again
Yes, you can connect 3 single phase transformers to form a single 3 phase transformer, Y or Delta.
I know of a specific example of a large power 13 kv to 230 kv transformer bank at a power generation station that is connected exactly that way. It is Delta primary and Y secondary.
 
When converting AC to DC, remember AC voltage is measured RMS (Root Mean Square) and not peak voltage. If you have 14 V AC and run it through a bridge rectifier, multiply 14 by the square root of 2 to get what the DC voltage will be. In this case, about 19.8 V DC.
 
ok ,remember you asked !! There is a British guy that has you tube tutorials ( targeted mostly at automotive ) he was rectifing three phase through 3 diode pairs & showing the result on a scope . My dad was into Army surplus stuff & in a large box of parts was a factory built rectifing fixture to accommadate 3 diode pairs , the diodes that are on it were TRW 1N 1188 & 1188 R . curiosity killed the cat ( & me ) so with an old ARRl book and a transformer from a 15 amp 6/12 V battery charger I have experimented with half wave / full wave / & full wave bridge . My shop has 230V 3 phase so the next logical step is to rectify 3 phase ! If you have ever shopped for small 3 phase transformers you will understand why I am wanting to build from 3 single phase units . Online internet info is currently being studied & one source says that for example the beginning & ending lead of each winding of the individual transformers has to be identified & when you hook the leads in either Delta or Y they ( all three have to be the same ) something about a phase shift . Of course the same applies to the 3 individual secondaries I warned you !!
 
When converting AC to DC, remember AC voltage is measured RMS (Root Mean Square) and not peak voltage. If you have 14 V AC and run it through a bridge rectifier, multiply 14 by the square root of 2 to get what the DC voltage will be. In this case, about 19.8 V DC.
That is correct for single phase bridge rectifier arrays, either straight or center-tapped secondaries, since the peak potential is √2 (about 1.414) and so is the power factor correction.

For a three-phase bridge the P-P remains the same (1.414) for the peak potential, but the correction for 3-phase is √3, or about 1.73.
 
As for individual transformers, @Red Dave is exactly correct. three individual single phase transformers can be connected to create a 3-phase array for step-down, step-up, buck, or boost applications. I asked about the desired output DC voltage since many of those very buck/boost transformers have 12/24 secondary voltages which could be suitable for your project. Without knowing the desired DC voltage it is a little difficult to suggest a specific path of either single phase or three.
 
Yes, you can connect 3 single phase transformers to form a single 3 phase transformer, Y or Delta.
I know of a specific example of a large power 13 kv to 230 kv transformer bank at a power generation station that is connected exactly that way. It is Delta primary and Y secondary.
I don't think you answered his question. 3 phase transformers do not need a common laminate core.
 
I can't find a step down 3 phase transformer specs : 250 V 3 phase input - 14 volt 3 phase output - 400 watts give or take / this will feed a rectifier with three diode pairs . maybe too far off topic for this forum , if so guide me to a forum please TIA
As joeysmith said, What are you trying to accomplish? It might give us a better idea of what would be the best way to approach the design. My thought is that Im not sure why you want to use 3 phase for such a small load (400 watt). The power savings would be so low that I would probably just build a power supply using a single phase or 2 phases in a delta configuration.
 