240 volt circuit

J. Schwiebert

Well-known Member
I put a new switch on my table saw. Now it runs but has no power. Having a senior moment. How do I check a 3 wire 240 volt circuit to see if I have 240 volts like I should or what else could it be as it worked good before! Thanks in advance. J.
 
Sounds like it may be missing one leg. If measure voltage to ground- should be 120v on each line switch post, and on each load side when turned on. Measure both of the line sides of the switch to each other should be 240. Measure both load sides when on should be 240 as well.
 
first, be very careful! because if you mixed up one hot leg with neutral or ground, then saw case may be hot. verify 240 between the two hot lines using a meter.
 
Likely you reversed a hot leg and the ground!

Turn off the breaker or unplug it!

The entire saw could be hot 120v to ground now, don't touch it!
 
i bought a new 220v switch for my garage heater a while back. i wired it what i considered the usual way. didn't put out any heat. dug switch instructions out of garbage and found it was to be wired completely different than what i had done. in my case, it was a simple wall switch. good luck
 
JS, you're a good man and can handle this I'm sure, piece of cake and I have a lot of those senior moments lol


1) If its a 240 motor but you're only sending it 120 SLOWWWWWWWWW PERFORMANCE LOL

To your question "How do I check a 3 wire 240 volt circuit to see if I have 240 volts like I should or what else could it be as it worked good before!"

2) A proper "3 wire 240 Volt circuit" that has NO NEUTRAL NOT INTENDED TO SUPPLY 120 would consist of 2 Hots L1 & L2 (Red & Black) plus a Bare/Green Equipment Grounding Conductor. NOTE I said Bare/Green Equipment Grounding Conductor NOTTTTTTTTTTT White Neutral. If a modern appliance (say maybe a dryer) requires BOTH 120 and 240 it now takes FOUR wires, 2 Hots, Neutral, Ground..............

3) HOWEVER if you accidentally switched/supplied the 240 volt motor with only ONE of the Hots (Red or Black, L1 or L2) and the Equipment Grounding Conductor (or a Neutral) THAT WOULD ONLY BE 120 VOLTS and it would run slow or not at all !!!!!!!!!!!!!!!!!!!!!!

4) You asked but I'm sure you know how to measure the voltage, it would read 240 across L1 & L2 (Red n Black) but only 120 from EITHER Red or Black to the Equipment Grounding Conductor (or a Neutral).

5) I have no idea if the third wire ran out is a Neutral (typically insulated White) or an Equipment Grounding Conductor (typically Bare/Green) but REGARDLESS the voltages above are the same as the N and G are bonded in the main panel. NEVER NEVER SWAP OR SUBSTITUTE OR MIX N MATCH NEUTRAL AND GROUND

6) A true 240 ONLY motor that uses no 120 3 wire circuit would be TWO HOTS and Ground



I THINK YOU WIRED IT WRONG AND ITS ONLY SEEING 120 VOLTS such as its wired to ONE HOT and Ground


NOTE when switching a 240 volt motor you should switch BOTH HOTS dont just cut/switch one of them.

NOTE that 240 volt circuit would be protected by a TWO POLE 240 Volt breaker...

PS since its an Electric question you may get a ton of responses (typically do) and Im sure I missed or forgot something so hopefully the other sparkies can add more to this..... or maybe we all agree ???? if so yayyyyyyyyyyyyyyyy

Nuff for now post back any questions BE SAFE NOW

John T
 
If you have mixed up which wires are hot and ground, pick the one you think is the ground and test with a volt meter each of the hot wires to ground. It should register 120v ea. Then to insure you have 240v use the volt meter one hot wire to the other and see if it registers 240v.

The wiring coming into your house has two 120v lines going to the breaker box and are kept separated. If the 240v line has been connected to one side of that box then you just have 120v. You have to have one wire from each side of the breaker box to achieve 240v. If you test the wire with a meter from one wire to the other and get zero that would indicate that problem.

Personally though I think if you wired a saw meant for 240v to 120v it just wouldn't start. I think the lack of power is a separate issue with the motor. It's also possible there is an issue with the size of the wire or the distance from the breaker box starving the saw for power. It's like running power tools from a too long extension cord.
 