Thanks for the help guys.
It is not true I do not like the answers given.
I just do not understand the answers given.
I'm not understanding why I can protect a 4 amp toaster with a 20 amp breaker but I can not protect a 20 amp A/C with a 40 amp breaker.
Also anyone that says it will not work because a disconnect must be within site of the A/C does not understand what I was asking because with my set up there will be a disconnect. I was just trying to run 2 units off a single disconnect.
But I think Ken gave me the answer I needed.
[b:654c4848f0]Also, most have a 'max circuit ampacity' spec on the tag.
To protect any warranty I would want to adhere to those specs.[/b:654c4848f0]
The page I was looking at just said needs a 15 amp breaker or needs a 20 amp breaker.
I took this to mean minimum size breaker.
But I did some digging in the technical pages and was able to find what Ken is saying.
It gives MINIMUM CIRCUIT AMPACITY and MAX.FUSE as 9/15 and 13/20 respectively.
So now I think Ken's advise will work best for me.
[b:654c4848f0]40A/8ga would go to a breaker box, not disconnects. Set up as a sub panel[/b:654c4848f0]
So I am now investigating something similar to the box in the picture.
It will allow me to put one big breaker in the main box and separate smaller breakers next to the A/C unit. It also will give me a spot to hook a single breaker for a 110 plug next to the A/C.
I understand I will need to run a 2 hots a neutral and a ground to the box and keep the ground separate from the neutral.
Thanks again.