I have been considering feeding an electric heater system with more than one homemade wind electric genertor. It is a three phase alternator that can be rectified, if necessary to pulsing DC, but the question is, can varying frequencies and/or voltage levels be joined onto a common bus? I cannot seem to find design data to see if this is possible, may have to bench test this idea. Anyone ever tried it? Leonard
 
Not a good idea as the phases have to stay in "snyc" or they will conteract each other.
Can you separate the system into 2 differnt sections then feed section 1 with one and section 2 with the second one?
 
Long thread about it within the last 2 weeks; may still be on one of the last pages; if not, it's in the archives.............
 
You can get generators and DC/AC converters that have the ability to synch up and produce power in paralell, but not cheap at all. Pretty much commercial stuff.
 
WHY do you need to tie them together for heating water?

Just tie each one to an appropriately-sized element(s).

Is this a car alternator?

Did you convert it to a permanent-magnet rotating field?
 
It can be done, we do it every day here when we Parallel to the system, but to do it with AC 3 phase generators is a fairly complex subject that I can't really cover here easily. You would have to match phase, frequency and voltage, then you need some way to govern the prime mover (your windmill) so that one generator doesn't hog all the load.

It is much simpler to do on DC. Though you still need to keep one generator from picking up all the load, but that could be done by voltage regulation on a DC system. Perhaps using batteries would absorb the spikes and valleys in wind availability.
 
If the generators and/or rectified to DC alternators all produce the "same voltage e.g 48V. You can parallel as many generators and/or alternators as you wish.
I would recommend a diode between each generator's + output terminal and the lead running to the load or battery. This will prevent a backfeed into a faulty generator/alternator. And to prevent the batteries from turning the wind turbine blades after the wind drops.
 
My windy hill is about a 1000 feet from where I would use the heat. I didn't think I could afford multiple wires from that site. All wind/electric alternators(homemade) would be similar unless I needed a larger one to "set the pace". Looks like I might be able to justify smaller gage wires if I used one line per generator. Thanks again for your comments.
Leonard in cold windy eastern Iowa.
 
How is the speed regulated on your alternators, or is are the speed and frequency governed at all? It would probably be easier to do this with three phase than single phase, because once you get one wind turbine going, you can use it to motorize the others; when a turbine is up to speed, you would unfeather its prop to bring it on line. The nature of a synchronous generator is that it MUST be in phase with any other generators to which it's coupled. So if you can control the speed of one generator, you can control them all.

Over the distance you need to run your wires, typical DC voltages would require very heavy cables.
 
Several small lines will cost much more than one main line.
You still haven't told us what the wind turbines are producing? If the output is 48V DC, there are no paralleling issues. Just use a diode at each turbine to prevent back feeding.
 