Gas furnace question....

Absent Minded Farmer

Well-known Member
What would cause a vacuum in the drain line when the furnace is running?

There's a black contraption on the side of the furnace that the line is attached to, that is holding water until the furnace shuts off & then the water drains out through the line. There was a rubber cap on the bottom of that black thingy that I pulled to help it drain.

If anyone needs more details, just ask.

Mike
 
What would cause a vacuum in the drain line when the furnace is running?

There's a black contraption on the side of the furnace that the line is attached to, that is holding water until the furnace shuts off & then the water drains out through the line. There was a rubber cap on the bottom of that black thingy that I pulled to help it drain.

If anyone needs more details, just ask.

Mike
That cap is a clean out for the trap (which is what the black thing is)
It needs the trap so it can drain properly because the draft inducer is pulling the flames through the heat exchanger causing a slight negative pressure inside it
 
Holler if you have further issues
My day job is hvac
Ok. Got the trap cleaned out as best I could. There's still a bunch of crud above the 90º bend up to the fan that I can't get to. Doesn't come off either. I pulled the sheet metal screw & it just swivels back & forth. Doesn't seem to be threaded & I don't see anything inside the cabinet that would hold it in place. Is that snap-fit inside the outlet coming out of the blower housing?

Otherwise, the furnace works ok. It isn't purging the water when it runs. Just percolates until it shuts of & then drains.

Don't recall that it's supposed to do that.

Everything else has been cleaned, blown through & checked for continuity. That's the only trouble spot so far.

Didn't even have the usual token dead mouse.

Mike
 
Ok. Got the trap cleaned out as best I could. There's still a bunch of crud above the 90º bend up to the fan that I can't get to. Doesn't come off either. I pulled the sheet metal screw & it just swivels back & forth. Doesn't seem to be threaded & I don't see anything inside the cabinet that would hold it in place. Is that snap-fit inside the outlet coming out of the blower housing?

Otherwise, the furnace works ok. It isn't purging the water when it runs. Just percolates until it shuts of & then drains.

Don't recall that it's supposed to do that.

Everything else has been cleaned, blown through & checked for continuity. That's the only trouble spot so far.

Didn't even have the usual token dead mouse.

Mike
Yes it should drain while running.
Got a picture of the setup?
If its draining after it shuts down it doesn't sound plugged up as much as it sounds the trap is messed up allowing it to suck air.

Its should seal it so it cannot gurgle while running.

Another possible cause could be the intake pipe is partially blocked causing a restriction through the combustion chamber


I have seen those traps Crack as well an cause that kina issue but normally they leak an make a mess when cracked
 