Billy Shafer onan generator

I got the Onan 6.5 nhd-fb/1m running and it puts out about 240v but the hertz shows about 132hz. Can you point me in the right direction, I know it should read 60hz. I check my meter with the power at an garage outlet and it was 60hz.
 
That is a 1800 unit. If it is showing those hertz. It would have to be screaming. Sounds like you are picking up noise from something. Can you post the full model and serial number. Let me do some checking.
 
I know that is the commercial version. But still that is an 1800 rpm unit. How are you reading the voltage and hertz. I have the manual for it around here somewhere.But it is not that much different than the RV unit. Do any of the fault lights come on.
 
I checked the output at the power wires and checked the speed with a tach, it is running 1800rpm. I have a manual. It starts and runs fine no lights except the normal ones.
 
Now thats one I can answer: It depends on how you're using the genset and if to feed your home as a backup genset, how many poles are being switched IE is the Neutral being switched or not??

If its configured as a Separately Derived Source, AND YOUR TRANSFER METHOD SWITCHES THE NEUTRALS, the gensets Neutral and Ground are bonded and also bonded to a Grounding Electrode such as a rod driven into earth. That's a bonded system, Neutral is bonded and NOT floating. That's similar to how your houses utility transformer and main panel are configured, Neutral bonded to ground buss and also to a grounding electrode such as a driven rod etc

In the event you're using it to power the home and are NOT switching the Neutrals IE genset Neutral is tied to house Neutral, leave the gensets Neutral floating (NOT bonded to case/ground) and bond the gensets case/frame to the homes equipment grounding conductor.

If you're simply using the genset to power up loads or appliances not tying into your home, it will work either with a floating or a bonded Neutral. I prefer a bonded system and many fault detection systems will alarm if theres no neutral ground bond. HOWEVER if its a construction site generator OSHA recommends if its a bonded genset DO NOT TIE TO AN EARTH GROUND ROD

If youre using a genset to power up tools or appliances FED FROM ONBOARD RECEPTACLES an earth ground is NOT required

Soooooooooo the answer depends on how youre using it. Many small portable gensest like Honda and I believe Yamaha come form the factory with a floating Neutral while others come bonded. If you tell me how you plan to use it and how you will transfer power if its to feed a home as an emergency backup I WILL TELL YOU TO BOND OR FLOAT THE NEUTRAL

NOTE there are even more rules and exceptions subject to use and transfer methods but this is enough for now.

John T Retired Electrical Power Distribution Engineer
 
I'm just trying to figure out if that would make my frequency reading to change. Trying to adjust everything but can't till I get this hertz problem figured out.
 
We have talked it over and all agree. It sounds like the meter is picking up noise from some other source. Some times this does happen when close to a power source. Try hooking a cord to your output leads then take a reading at the other end of the cord. See what you have then. Ten feet should do it just get it away from the generator. Do you have any fluorescent lights around. They can be a source of problems. Hook up some sort of load see how that does. Hair dryer,drill or some other item. Let me know.
 
April 1998 is one of the early ones. I can check the PSB files for any problems noted. Shows you how the old stuff was much better than the new. 20 years old and still going.One reason why everyone is looking for them.
 
I was ONLY answering your question about the Neutral and Ground. Billy has you covered concerning the frequency.

John T
 
Mornin Billy, I don't view it as any "fight" there's simply a right and NEC way to do it or an incorrect unsafe method, but to any lay person I can see how its confusing grrrrrrrrrr MANY small portable gensets come from the factory with a FLOATING NEUTRAL for good reason. In RV's with onboard gensets the AC distribution panel has separate insulated and isolated Neutral and Ground busses which is why those Gensets are configured as a Separately Derived Source with a Bonded Neutral. If a portable genset is used to feed an RV it should likewise have a Bonded (non floating) Neutral, and actually be bonded to a grounding electrode...?..

PS so far since I correctly adjusted my Generacs governor linkage I'm still running 60 HZ at 115 + under a heavy load yayyyyyyyyy

John T
 
Mornin John. Cloudy and 65.

I understand but you know how some inspectors can be. I got refused an a 120/240 single phase system. Because it had no phase rotation lights. Me and sparky tried to explain the system. But the rookie insisted we had to have lights. So we rigged up a light panel for him. He was happy we passed and he left.
 

reminds me of the miller welder/generator... with an 2 cyl onan engine.

It runs very fast in the weld position(3600), and very slow in the gen position(1800) and even slower at idle.
 