Electrical service grounding question

  • Thread starter Thread starter e
  • Start date Start date

e

Member
To give you guys some background, I'm upgrading the electrical service on our farm to 400 amp. The current system comes in to a central pole, then branches out to each building. The new system will be underground and will come into the shop. From the shop, I will be running from one main panel to the barn, house, etc.

What I'm trying to determine is if I should have grounding rods for each building, or, should I run two hots, a nuetral, and a ground from each building to the main panel. My plan has been to ground each building seperatly with two 5/8" 8' rods etc etc. It feels better to me to ground as close to the point of use as possible. The distance I need to run from the main panel to each building is about 150'.

Now my other question pertains to grounding the barn. Do I need to give any special consideration to grounding a building with livestock? Would it be better to run a ground back to the main panel to minimize the potential for stray voltage?
 
Farm wiring code differs from house wiring, and you are mixing the two. Here in NY, if I followed code, I could do it either way. House wiring requires and allows only one ground system. Farm wiring allows grounds at each building if desired.

Here in NY I'd never have the main power going to an outside building first. It changes the electric rate from household to commercial or farm which is higher. Most farmers in my area run the main power to the house first. Then to the farm buildings, and this way the farm runs on the lower household rates. Maybe it's different by you?
 
The code now requires that you run a ground conductor from the service to each sub panel. Grounding and bonding at each sub panel is no longer permitted. Your ground rods and bonding with the neutral should only be done at the main service which sounds like it will be in the shop. It is very important that all the sub panels have the neutrals and grounds seperated on different terminal bars and that they NOT be interconnected or bonded. If you are reusing existing equipment in the other buildings they may have to be rewired to make sure this is done. Not a big job but a big deal.
The size of the ground conductor will be based on the size of the breaker feeding each panel.(Table 250.122 in the NEC) You can find information about all this in Article 250 of the NEC. I would encourage you to upsize the conductor for the ground. Also, if your runs to the other buildings are very long you may want to calculate voltage drop and consider upsizing those as well.

It sounds like you are aware of the importance of grounding. Bonding is a little more complicated. You may want to have a licensed electrician take a look at your job when it is done.

Also, you can find a lot of information on grounding agricultural buildings on the internet. Stray voltages seem to bother cattle and horses more than other stock and some of the soloutions need to be done during construction such as grounding mats in concrete and such. Attention to grounding what is there will likely solve most of your problems.

I got called to a farm one time for a service call. The guys hogs were dying for no apparent reason. Turned out that improper grounding and bonding (along with an underground splice made in a coffee can filled with tar)had electrified all of the metal siding on his barn and when the hogs bushed against it with their feet grounded in the wet dirt they were freezer bound. Lucky it wasn"t him.

Good luck with your project.
 
I don't know what code is being used and/or required where the poster lives. Different states use code versions of different years.

Here in New York current code for farm wiring calls for grounding at the house, each building, and any main service pole (with some exceptions).
 
(quoted from post at 13:21:59 12/03/09) To give you guys some background, I'm upgrading the electrical service on our farm to 400 amp. The current system comes in to a central pole, then branches out to each building. The new system will be underground and will come into the shop. From the shop, I will be running from one main panel to the barn, house, etc.

What I'm trying to determine is if I should have grounding rods for each building, or, should I run two hots, a nuetral, and a ground from each building to the main panel. My plan has been to ground each building seperatly with two 5/8" 8' rods etc etc. It feels better to me to ground as close to the point of use as possible. The distance I need to run from the main panel to each building is about 150'.

Now my other question pertains to grounding the barn. Do I need to give any special consideration to grounding a building with livestock? Would it be better to run a ground back to the main panel to minimize the potential for stray voltage?

you ask, "Would it be better to run a ground back to the main panel to minimize the potential for stray voltage?"

You can do that. The NEC has several instances of info on this topic & one must take care not to mis-apply any one instance to the wrong situation......it can be confusing.

Keep this all important over-riding statement in mind when setting up your grounding scheme: "Never create a situation where neutral load current is allowed to flow in the safety ground conductor."

How does that apply to your question, you might ask?
IF you choose to run both a safety ground & a neutral to your livestock barn, then to avoid having neutral load currents flowing in your safety ground, the two 'grounds' (neutral & safety) MUST be separated at the barn. Note, since they are common at the service entrance panel, if they were to be tied together (common) at the barn, now the neutral conductor and the safety ground conductors would simply be in parallel (essentially one conductor composed of 2 strands)...no good!

nec PARA 250-24 (A), EXCEPTION #2
 
Your best bet is to use a local electricial who is familiar with local code; or visit with the local inspectors. One county to the next can seem to interput the same code in different ways.

You've identified some of the issues that can snag you.

Code much prefers using the 4 wires, including running a safety ground from the central box _without_ bonding that ground in any of the other boxes - as someone mentioned.

There is a farm exception where you can do a ground rod at each building & not run the 4th wire to each location. Your local inspector may view this differently, so best to check with them.

Any building with a waterline connecting it to another building also has special considerations. With livestock and water lines involved, stray voltage becomes a bigger issue. You might want to get good local advice on how to handle this.

Livestock buildings need the main box for the building located _outside_ the building. They had too many rust through & the guts corrode when located inside.

All of this can be a tad different in your location. There is room for the inspector to follow things differently.

When I had rewiring done a few years ago, it was all 3 wire, local ground rods at each building, nothing special for the barn other than I needed the outdoor box on the barn. That was how the local inspector wantd it, that was how my electrician was familiar doing it, everyone got along, and my 'inspection' consisted of the inspector looking at 4 of the 14 boxes that were installed. He got bord, got my sticker, & all was fine.

--->Paul
 
In years past, you could get by with running ONLY 3 wires out to a remote building for 120/240 volt single phase 3 wire service, that would be 2 Hots (L1 & L2) and a Neutral (a grounDED conductor), and you would (as usual) drive a ground rod(s) at the remote location. HOWEVER the modern practice is to run 4 wires out to the remote building 2 Hots (L1 & L2) a Neutral (a grounDED conductor) and the Equipment safety ground (a groundING conductor)

THE TROUBLE IS different jurisdictions may or may not have adopted different versions of the NEC SO YOU HAVE TO CONSULT YOUR LOCAL AUTHORITY versus relying on most of us here. If they say run 3 then do that but if they say run 4 then you have to do that.

Animals are so sensitive to electrical current and shocks that old bossey may refuse to drink from an automatic watering device if it has a metal case that has a voltage potential higher then mother earth shes standing on, so there are indeed certain limited exceptions when it comes to grounding in ag buildigns used to house livestock. With paralell Neutral and phase wires and Equipment Ground Conductors ran a long distance to the outbuilding the capacitor affect can cause the equipment ground to have a potential higher then earth OUCH for old Bossey lol Soooooooo the exceptions allow you a method to bring that back down to mother earth so the waterers metal frame is the same potential as earth.. I believe that was the basic theory anyway (its been a longggggggggg time)

NOTE check with your local authority, although I used to design secondary power distribution systems as an EE Ive been long retired and rusty on current NEC so NO WARRANTY this is my best recollection ONLY

best wishes

"Stop Global Whining"

John T
 
Altho it would have been cheaper and easier to locate te main panel in an outbuilding we had to install the main panel in the house and subfeed from there.

steveormary
 
e,
You"ve recieved a lot of advise, most of it contradictory.
I recommend that you buy the latest version of a book called "Wiring Simplified"(see the link)and see how the 2008 NEC applies to your specific situation.
If you"re not comfortable interpeting the NEC itself, one of these books can be a big help.
If you"re not comfortable working from one of the "Wiring Simplified" books, you may need to reconsider hiring an electrician.

Good luck,



Art
www.wiringsimplified.com
 
(quoted from post at 21:12:49 12/03/09) e,
You"ve recieved a lot of advise, most of it contradictory.
I recommend that you buy the latest version of a book called "Wiring Simplified"(see the link)and see how the 2008 NEC applies to your specific situation.
If you"re not comfortable interpeting the NEC itself, one of these books can be a big help.
If you"re not comfortable working from one of the "Wiring Simplified" books, you may need to reconsider hiring an electrician.

Good luck,



Art
www.wiringsimplified.com
Nothing contradictory in what I said.
"Keep this all important over-riding statement in mind when setting up your grounding scheme: "Never create a situation where neutral load current is allowed to flow in the safety ground conductor."
"
 