Hey 55 50 Ron
John T
Sorry I missed your last response and question to me over on the previous page, so here's my answer..
You asked: From your description, it needs to be the NEMA 14-50R as is used in an RV park's power pedestal. I think it would be useful for me to photo the inside of the 200 amp panel and post the photo here. I do understand basic wiring, but I tend to get puzzled with neutral and ground differences. Thanks to all who are contributing to this.
MY ANSWER:
YES you need to install a 250 Volt 50 Amp NEMA 14-50R Three Pole Four Wire Grounding Receptacle. Thats
whats used in 50 Amp RV Park Pedestals
That requires FOUR 6 Gauge Copper conductors FROM the panel TO the receptacle, namely
Red Hot L1,,,,,,,,Black Hot L2,,,,,White Neutral,,,,,,,Green Equipment GroundING Conductor
The Red & Black are connected to a TWO Pole 50 Amp Circuit Breaker in the Panel
The White Neutral is connected to the Neutral Buss in the Panel where all the other White Neutrals are
connected
The Green is connected to the Ground Buss in the Panel
NOTE On some MAIN distribution panels the Whites and Neutrals are ALL connected to a single common Buss
where ALL Whites and ALL Neutrals are attached
NOTE Ifffffffffff the panel in question happens to be a SUB PANEL fed from a MAIN Panel it will have
separate Neutral and Ground Busses
NOTE I have no idea what receptacle is there and if it is fed by three or four wires ??????? If its ONLY a Two Pole Three Wire Grounding 240 Volt ONLY it may only have three wires Hot Hot Ground. If so thats NOT enough wires it doesnt have a Neutral.
NOTE I have no idea what the panel is?????? Im talking like its a 120/240 Volt Single phase Three Wire, if notttttttttttttt things can change post back more info !!!!!!!!!!!!!
To plug a 50 Amp RV all you need is a properly wired NEMA 14-50R Three Pole Four Wire Grounding receptacle wired with FOUR 6 Gauge Copper wires to a 50 Amp TWO Pole breaker in a panel. Black n Hot to the two poles on a 50 amp breaker,,,,, White to Neutral,,,,,,,,, Green to Ground EASY PEASEY
Your Panel if Main may or may not have separate Ground and Neutral Busses (which are bonded if at main panel) or if a SUB Panel definitely separate Ground and Neutral Busses, but regardless you can use either to feed your receptacle. The Neutral Buss is where the Whites are attached,, the Ground Buss is where the Bare and Greens are attached....
Hope this answers your question
John T Long retired n rusty power engineer (and NO idea what panel is there) so NOOOOOOO warranty but believe this is still true Live from Gulf Shores
PS I forgot you asked about Neutral and Ground, this may help:
Neutral (White) is a GROUNDED live conductor that carries normal return current. NOTE the (Black) Hot is referred to as the UNgrounded Conductor.
Equipment GroundING Conductor (Bare/Green) is ONLY for carrying FAULT CURRENT so theres a return path so the Breaker can trip to de energize the circuit and save a life
There can be ONLY ONE NEUTRAL GROUND BOND often in the main panel or first means of disconnect
The Neutral (BOTH HV Primary as well as LV Secondary) is attached to a Grounding Electrode (such as but not limited to rods driven into earth) for surge and lightning protection and to keep the grid at a common low voltage reference IE mother earth.
Clear as mud ????
Take care Ron
John T Gulf Shores just had breakfast in an Escapees (SKP) park where we are members. We are Dry Camped (have all the solar panels and lithium batteries we need) but have access to water and a dump station all for a whopping $7.50 per night yayyyyyyyyyyy Had supper last night at the Foley Alabama American Legion
John,
I'm a little slow this morning. Outside temp is +4F in MN. Thanks for all the input. I'll get this done when the weather hits an above-freezing temp.
Thanks to all these electrical gurus who are helping. Much appreciated, folks.