My welders all have 3 prongs, but are older. I believe this 4 prong gives you neutral and ground.What is this plag used for? I don’t think I’ve seen a four prong plug before.
Thank you,
Glenn F.
14-50P for 125/250VWhat is this plag used for? I don’t think I’ve seen a four prong plug before.
Thank you,
Glenn F.
What I heard was that for modern day 220 appliances, which have electronic controls, they had to be able to split off 110 volts to run the electronics, which didn't work when only a ground was used as the 3rd leg. Or was it the neutral as the 3rd leg? I obviously don't know what I'm talking about! steveMy welders all have 3 prongs, but are older. I believe this 4 prong gives you neutral and ground.
Almost. There was no true equipment ground (unless run to a pipe or separate rod. The neutral was used as the 120v leg. The 240 was across L1 to L2 with the Neutral not used for the higher voltage. JimWhat I heard was that for modern day 220 appliances, which have electronic controls, they had to be able to split off 110 volts to run the electronics, which didn't work when only a ground was used as the 3rd leg. Or was it the neutral as the 3rd leg? I obviously don't know what I'm talking about! steve
Thanks, Jim. So to continue this, is the 4th contact on the modern plugs for ground? And why then does the 3 wire plug on my welder have two hots and no neutral? Because to get the 240 for the welder, you only need the two hots, and the third leg is equipment ground? steveAlmost. There was no true equipment ground (unless run to a pipe or separate rod. The neutral was used as the 120v leg. The 240 was across L1 to L2 with the Neutral not used for the higher voltage. Jim
Even though grounds and neutrals land on the same terminals in the breaker box, a neutral has to be an identified conductor (like the white wire on a 120 V circuit) to differentiate it as a current carrying conductor as opposed the ground.Thanks, Jim. So to continue this, is the 4th contact on the modern plugs for ground? And why then does the 3 wire plug on my welder have two hots and no neutral? Because to get the 240 for the welder, you only need the two hots, and the third leg is equipment ground? steve
The neutral to the 3 wire device is from old code era that allowed it to carry that responsibility even if there was no actual load flowing in it. It also provided a path for induced voltage from the secondary windings and arc EMF. JimThanks, Jim. So to continue this, is the 4th contact on the modern plugs for ground? And why then does the 3 wire plug on my welder have two hots and no neutral? Because to get the 240 for the welder, you only need the two hots, and the third leg is equipment ground? steve
To be clear, three prong, three wire receptacles do not have a neutral connection. 250V 3 wire, just two hots and ground. This is not something old or obsolete. The old and obsolete was three wire 250V with ground being allowed to place small 120V loads across one hot and the ground, thereby causing current flow in the grounding conductor and raising it above ground potential. The grounding conductor is only allowed to carry fault current now.The neutral to the 3 wire device is from old code era that allowed it to carry that responsibility even if there was no actual load flowing in it. It also provided a path for induced voltage from the secondary windings and arc EMF. Jim
Those three replies just explained it the way I thought it worked, but wasn't sure. Thanks, Jim, WP, and NoDak.To be clear, three prong, three wire receptacles do not have a neutral connection. 250V 3 wire, just two hots and ground. This is not something old or obsolete. The old and obsolete was three wire 250V with ground being allowed to place small 120V loads across one hot and the ground, thereby causing current flow in the grounding conductor and raising it above ground potential. The grounding conductor is only allowed to carry fault current now.
The neutral is the grounded conductor, is not connected to the metal chassis of most devices and is insulated all the way back to the service panel where the bond to ground is. The neutral is expected to be carrying current and not at ground potential which is why it is insulated. The grounding conductor is commonly uninsulated and is typically connected to metal equipment chassis.
Stevie, yes the 4th contact is the Equipment Grounding Conductor. However if a welder requires straight 240 volt only a 3 pin plug suffices for the two hot 240 volts while the third is the safety ground.Thanks, Jim. So to continue this, is the 4th contact on the modern plugs for ground? And why then does the 3 wire plug on my welder have two hots and no neutral? Because to get the 240 for the welder, you only need the two hots, and the third leg is equipment ground? steve
Stevie you’re asking good questions and that’s the best way to learn. In the old days with only two hot legs and a ground there would be 120 from either hot to ground so they were using the ground as a live current carrying conductor and the ground could be bonded to outer metallic case frames of appliances whic you touch and that could be a hazard. So modern wiring used the insulated neutral to carry return current not the bare geeen ground wire which may be connected to the tools case. Ground for fault current only neutral for live normal return curent it’s insulated so you don’t touch it John TWhat I heard was that for modern day 220 appliances, which have electronic controls, they had to be able to split off 110 volts to run the electronics, which didn't work when only a ground was used as the 3rd leg. Or was it the neutral as the 3rd leg? I obviously don't know what I'm talking about! steve
Reality was a hazard! and other than that could still be! JimStevie you’re asking good questions and that’s the best way to learn. In the old days with only two hot legs and a ground there would be 120 from either hot to ground so they were using the ground as a live current carrying conductor and the ground could be bonded to outer metallic case frames of appliances whic you touch and that could be a hazard. So modern wiring used the insulated neutral to carry return current not the bare geeen ground wire which may be connected to the tools case. Ground for fault current only neutral for live normal return curent it’s insulated so you don’t touch it John T
John, So, if I want to use 110v (one hot leg), my neutral will be running current, but if I want only the 220/240, (both hot legs) the neutral won't have any current in it? I'm ignoring the ground circuit in this. steveStevie, yes the 4th contact is the Equipment Grounding Conductor. However if a welder requires straight 240 volt only a 3 pin plug suffices for the two hot 240 volts while the third is the safety ground.
Remember The grounded conductor aka neutral is for normal return current while the EGC is ONLY for fault current.
Got it ?? If not post back
John T
We sell tractor parts! We have the parts you need to repair your tractor - the right parts. Our low prices and years of research make us your best choice when you need parts. Shop Online Today.
Copyright © 1997-2025 Yesterday's Tractor Co.
All Rights Reserved. Reproduction of any part of this website, including design and content, without written permission is strictly prohibited. Trade Marks and Trade Names contained and used in this Website are those of others, and are used in this Website in a descriptive sense to refer to the products of others. Use of this Web site constitutes acceptance of our User Agreement and Privacy Policy TRADEMARK DISCLAIMER: Tradenames and Trademarks referred to within Yesterday's Tractor Co. products and within the Yesterday's Tractor Co. websites are the property of their respective trademark holders. None of these trademark holders are affiliated with Yesterday's Tractor Co., our products, or our website nor are we sponsored by them. John Deere and its logos are the registered trademarks of the John Deere Corporation. Agco, Agco Allis, White, Massey Ferguson and their logos are the registered trademarks of AGCO Corporation. Case, Case-IH, Farmall, International Harvester, New Holland and their logos are registered trademarks of CNH Global N.V.