How did water heater problem get resolved? Have one of my own after guy did install. No voltage across the input that should be 220, but 119 from either to ground??
 
119v to the ground is meanless. Go back to the breaker and
measure 220v. If not, you may have a defective breaker..One time
I had a defective load center another time I had a defective
main breaker.
You need 220v between two power wires for it to work..
 
You have one leg from the breaker dead, what you are reading is voltage on one leg, feed back on the
other.

Check at the breaker, should get 230v or so across the breaker terminals. Should also get 230 across the
main breaker or the main input terminals.
 
I had a new 220V window A/C that wouldn't work,same deal, 110V and 110V. Someone told me to check for 220V and when I did I had 110V. 60 amp disconnect (fuse type) was bad. I also have seen boxes that would allow you to put both hales of the 220v breaker on the same leg in the box=110V on both sides and only 110V across both.
 