Hydronic Heating system expert?

showcrop

Well-known Member
For two or three months now, I have been noticing a thudding noise when my furnace comes on. It does it when a zone is calling for heat, and when it is just bringing itself up to temp. It sounds almost like an old steam system clunking. The expansion tank has 2/3 air, the air purging unit is about 2 years old and has no air in it. The pressure is around 20lbs. the system was opened to replace a zone valve about 14 months ago but this started only recently.Any ideas?
 
Are you SURE the boiler temp/pressure gauge is working/accurate?

In other words, do you REALLY have 20 PSI of system pressure and under 200ºF temperature?

The standard water pressure for a one or two story home is 12 PSI, but 20 would be even better as far as NOT making noise. (Safety valve blows at 30 PSI.)

Are you SURE there's no closed valve or other restriction between the furnace fitting/air separator and the expansion tank?

Also, is the expansion tank a "bladder tank" or a simple old-fashioned tank?
 
I am presuming that you have an oil fired boiler. That being said it sounds like you need to call your service man. A partically pluged nozzle, low pump pressure, partically pluged filter,mis-adjusted burner air intake, or if you had mega snow fall check your chimney. It might be covered with snow. BOTTOM LINE CARBON MONOXIDE KILLS.
 
Is that zone heating good? If so hot water loop is probably ok with no air in loop. Is the boiler pulsating when it first fires. If so may have delayed ignition caused by bad nozzle or electrode setting. May be carbon built up on burner cone. Oil pump may not be cutting off allowing oil to drip in combustion chamber. Also dirty blower wheel on burner will cause problems. This for oil fired boiler. DH
 
Bob, Thanks for your response. I pulled the expansion tank which is a bladder type, to make sure that it's opening was clear. I have encountered them being plugged before but it was open and the bladder was right there and flexible. when I refilled I watched the gauge climb to 12 lbs. and the air catcher let some air out. When I turned the burner on I watched the temp go from 160 to 200 and the pressure climbed about three more degrees. It didn't make the clunking sound so I will have to monitor it. Probably in the spring I'll put on a new gauge and boiler feed valve.
 
You shouldnt be able to see the bladder in the expansion tank unless it is shot also what type of zone valves do you have on this boiler? might also have something to do with the sound
 
Good evening,

I don't know what kind of boiler you have, but it's worth remembering that a typical hydronic heating reset schedule would only allow circulating water temps as high as 180 if outdoor temperature were as low as 0, and would then modulate the water cooler as the OD temperature moderated. That is to say, your circulating water is too hot. If you have any restriction in flow, odds are that you are making steam in those areas of your boiler that have restricted flow and therefore low velocities (ie approaching 0 fps.) This is common, especially in residential boilers, especially the old vertical copper heat exchangers and now the instantaneous low mass boilers. Were it me, I would lower my operating control to about 155 and my static pressure to 12 psi, which is all a typical residence needs to ensure system fill and see if the problem resolves.

Good luck,

Oxford
 
What kind of boiler? Old, newer? I have a Utica boiler, made in Utica NY. Alot of people say Well McLaine are the best,, Mine seems fine. Do you have air in the system? Is it hot water baseboard? Mine runs at 180 degrees 12 psi.
 
Some of the old ones like mine will run 200 degrees. But I added another stat and dropped temp to about 180 at zero degrees(adjustable, easy and not expensive.) If you ever altered any piping you probably will get noise from expansion and possibly not using the correct hangers. Air in system, as you know, will give you noise. As someone mentioned you do have expansion tank, right? Other wise tank in attic has to be drained occasionally if waterlogged for proper function. Only really big noises I recall was when pump was failed and only thing shutting it down was high temp limit. It was almost walking around the floor. No expert, just Hvac guy user.
 
The best place to go for help about heating is "heating help.com" They have a "wall" to post questions on and it is answered by heating pros from all around the country. Good luck!
 
Oxford, Thanks for the reply. My boiler is a 21 year old Vesta steel unit. My thoughts have been that I was producing air in there somewhere. I recalled that something else that has changed is that I replaced the half burned baffles in the flue tubes last fall. I expect that this would make the temperature higher a little lower down in the unit. Couple that with the temp being a little high could be causing a little boiling to be going on. I have reduced the temp so as I sit here at the 'puter just above it I will hear what difference it makes.
 
That's strange, I've probably installed a hundred bladder tanks over the last thirty years, and whenever I looked the bladder was right there in the opening. Once when I brought one in for warranty replacement the counter man said that the factory (Amtrol) had called and was wondering what we were doing with all the tanks.
 