PTO-driven back-up generators - advice requested.

jgc

Member
Do the PTO-driven back-up generators work well?
(Assuming that the tractor driving it has adequate horsepower and good speed regulation.)

I was looking at a significantly oversized diesel gen-set(40KW) for my small property.
After looking at the numbers, I can buy a 45 horsepower utility tractor with loader and a PTO generator for about 50% more than the big genset.
I can use the tractor year-round, the genset probably would be needed half a dozen times a year!

I have been advised to buy the more expensive 1800 RPM models for longevity.

Advice from anyone with first-hand experience using these generators would be greatly appreciated.

Thanks,
JGC
 
All good from what I see on your post.
Here are a couple of links for transfer switches.

http://www.generlink.com/downloads.cfm

http://www.reliancecontrols.com/ProductDetail.aspx?TWB2012DR
 
As soon as I get back home from China this weekend, I"ll post some info about my 25/40 KW Genny. All you said is true.

Frank-IN-Beijing
 
I found a used 25 KW pto generator priced really right. In 11 years in NE Iowa winters, I've used it maybe 3 or 4 times. I use my JD 855 on it (about 20 pto hp, 540 rpm). Sure it's way more generator than that little tractor can handle, but that's OK, I just don't load it up. Once we had a week long power outage. With the generator we could pump water, run the blower motor on the LP furnace, keep the refrigerators and freezers cold, keep the sump pump available, have some lights, stay in our house and didn't have to drain down the plumbing and abandon ship. We didn't, couldn't, run everything at once, but could run all or most of the above at the same time. We couldn't run the electric stove nor the heat pump. Of course had we had resistance heating and an electric water heater they would have been no-no's as well. The weather wasn't real cold for it was at spring ice storm time. I run it only about 3 or 4 hours per day. You will find that buying electricity is much, much lower cost than burning gasoline or even Diesel fuel to generate your own. Keeping the voltage and frequency close enough was no problem. I have a little hand held device by the trade name of Kill-A-Watt that really helps with this. I don't know where you live but would guess you'd use it only once every 3 or 4 years, not use it 3 or 4 ties a year. Remember, reliability is much more important in a stand-by generator set-up than is durability. Probably the biggest draw back of a pto powered stand-by generator is that you have to go out and hook it up when you need to run it. Sometimes the weather isn't conducive to that! With my current set-up, the rig has to set outside to run. I've thought about running a heavier line out to my shed so it could could run and be hooked up inside but copper is pretty high these days. The generator is currently mounted on a little 4' X 4' two-wheel trailer. I have the house wired with a sub-panel for those circuits that can be powered with the generator and there's an outside socket for plugging the generator in. Of course there's a safety switch to keep from back-feeding the power company's line. All this works for me and I wouldn't be without some sort of electrical back-up.
 
Frank, What in the world are you doing in Beijing? You're way off home base! Business or pleasure? Sometimes they can be the same, but maybe not in China. I was there about 30 years ago. There was one western style hotel in the whole country, everyone (men and women) wore Mao uniforms, there were almost no cars but bazillions of bicycles. Understand it's way different now. - Leon
 
A big generator will waste a lot of fuel unless you put a steady max load on it. That will not be possible when hooking a big unit to a common household.

I've got a 17KW PTO generator and even that is wasteful when running a house. Hooked to a 35 horse tractor . . sometimes if works a little hard and most of the time, hardly at all.

A diesel engine run at 1/3 its rated max power loses twice its fuel efficiency.

About 1800 RPM? They run half the speed of an engine running 3600 RPM so in theory, it will last longer. The super HD two-cylinder Detroit Diesel 20KW gensets run at 1200 RPM. Lots around for sale - rebuilt and fairly cheap.

The only way to have a generator power a house and "load-match" is . . . to have an inverter generator, or . . . any generator hooked to a battery bank and then powering the house with inverters. This way the gen is only run once in awhile and when it is - it is run at max capacity and max efficiency (just to recharge batteries).

I realize you want back-up so maybe fuel efficiency is not a big concern. A 15 KW should be more then enough to run a house unless you have some heavy AC appliances. I run a 17 KW PTO generator with a 35 horse tractor and easily run my house and shop where I do some arc-welding.

One problem with AC generators is they only can run a one speed in order to make 60 cycle current. On the other hand, an "Inverter" generator makes DC and inverts to AC and can run at any speed and be much more efficient.
 
Why on earth would you go that oversized ?

Are you running a grocery store during a power outage ? grow lights for illegal plants ?
Stay close to the size you need.

And we have a pto model that runs at 3600 rpm. this thing is noisy !! try and go 1800 rpm
 
I suspect some people have heat-pumps, electric heat, electric hot-water, etc.

That is pretty rare in my neck of the woods (central NY). Electric rates are so high that electric heat is almost non-existant. And electric hot water? It was rare but now coming back to a degree. 30 years ago the power company was giving away gas or propane hot water heats trying to wean people off of electric hot water.

I've run my house in a pinch with a Homelite 4400 watt generator. I had to make sure big appliances only came on one at a time but it did the job including my 3/4 horse 220 volt well pump.

My 17 KW PTO generator hooked to a 35 horse tractor easily runs my house and rarely even grunts.

Big gensets are incredible pigs on fuel usage unless they are run at a max steady load.
 
45HP on a 30KW generator is not overkill for some applications. If it's an all electric house with electric clothes dryer, well pump, sump pump, 2 fridges, two freezers, electric water heater , electric stove and lights. That is what 's required to provide near grid quality power to limit light dimming.
Running the pto generator 3-4 hours a day and then just run a phart can 6500W gasser the rest of the time.will give the best of both.
 
I have an older 15/25 1800RPM unit. It will run the house and shop with a 20 HP tractor. One time the tractor ran all night. I was worried about running out of gas, but had plenty to spare. I imagine the 1350 engine RPM @ 540 PTO has something to do with that.
I wouldn't be without it.
It will start and run a 10 HP blower motor on a bin/grain dryer, but even the 40 HP tractor won't do it- have to put the 60 HP on it.
 
I bought a 15 KW pto generator from Harbor Freight for about $1,500.00 for emergency backup. Only had it hooked up once to the house which is when the electrician made the hook up and installed the transfer lockout. Our house is all electric and the generator is adequate but running the furnace really takes the power. Just couldn"t say run furnace and oven at the same time. No electricity no water, no refrigerator so its great to have some backup. They recommend at least a 30 hp tractor.
 
Hi Everyone,
Thanks for taking the time to provide feedback.
It is very helpful.

I have an older portable Generac 7kw generator that I believe is quite conservatively rated. It claims to put out 12.5 KW peak for starting motors, etc.
This generator really struggles to start our 2.5 ton air-conditioner. I got all "lathered up" about this brand new 40KW genset because it had a lot of optional features including coolant heater, anti-condensation heater for the sound-reducing enclosure, etc, etc, and it is priced well below list because it was ordered incorrectly for a government customer.

I realize that it is over-kill, but it would definately run everything without a problem.

Take-aways:
-buy an 1800 RPM unit
-over-sizing wastes a lot of fuel.
-buy the heavy duty model - light duty units may not last,
-look into used units,
-opinions vary as to what is enough power.

Thanks again,
JGC
My Blog
 
Yes opinions will vary as to what's enough power.

But that's mainly because we have no clue what you are trying to run with it.
This can be calculated.
 
(quoted from post at 04:43:15 10/12/12) Frank, What in the world are you doing in Beijing? You're way off home base! Business or pleasure? Sometimes they can be the same, but maybe not in China. I was there about 30 years ago. There was one western style hotel in the whole country, everyone (men and women) wore Mao uniforms, there were almost no cars but bazillions of bicycles. Understand it's way different now. - Leon

It was a vacation, flew to Anchorage, then cruised to stops in Japan, Russia, and China. Ended in Beijing for a few days. Place is all modern now, Shanghai has the most buildings over thirty stories in all of Asia. The three cities in China we visited were so modern that there was not much in the way of old world charm to see unless you visited the historic sections like Hutong in Beijing. No Mao suits, mostly Armani and iPhones. Was a very informative and interesting trip. Lots of cars, lots of Chevys and Buicks in fact. Nicest MArriott downtown I"ve ever stayed in, and the airport Hilton was 5 star, too.
 
We have a Winpower 30KW 540 pto with a manual transfer switch at the meter pole. Originally to back up our dairy operation it's a nice option to have when the power is out for a while. But since we are in the middle of a main line with lots of houses on it we haven't been out for more than 2 hours for probably 10 years. It is also nice for plugging in the welder or other power needs away from the outbuildings and doesn't have another engine to maintain.
 

That is exactly what I do. I have the pto unit, a "Dayton" (I think it is Generac relabled and sold through Graingers) which is 25KW and 50KW surge, to use for long term outages,

Gen110V.jpg


I mounted it to a TSC three point carry all, and welded on some hooks for holding the industrial cable that hooks it to the house, along with a rack for the pto stub shaft and tarp hooks so it stays clean when stored for the 99.9995% of its life.

Carry-allroof.jpg


I keep a 6500 watt Coleman in the garage next to the panel. Both use the same Anderson power Pole connection plugs into my manual transfer switch.

HOMCGK2CutOverKit.jpg



Here in N. Florida, we'll get a late afternoon storm that knocks power out for three or four hours, 10 or so times a year, and the little gas unit will keep the TV, lights, computers, ceiling fans and such running just fine for a short time. If we we get a major event like a hurricane, the large unit gets hooked up because by the third or fourth day the house starts to get pretty warm when missing its 5 and 3 ton AC units. Been a while since we had such a long period of outage, but we were in Italy for two weeks in '05 and the daughter had to house sit in our powerless house for 11 days. She had places to go and stay, so she just emptied the refridgerator. That's when I started looking for a large pto unit, and I found one 30 miles away, still in plastic wrap. The fellow bought it for hurricane use and relocated to a northern city before he could even hook it up. It weighs as much as a 455 Olds V-8, so it's too heavy for my 855 to lift, though it would spin it at lower power use if needed. I use it on the 4310, and have even run it with the VAC Case, again at lower power output. It's nice to burn in different engines now and then, but I pretty much just use my M&W dyno for that.

The 4310 will run every light in the house, while pumping water, with the washer running, but if you hit the start button on the clothes dryer, it will slowly grind to a halt, so I know the tractor is a little short on power, but that's not a bad thing. I just will need to manage the power a bit and not run everything all at once, or, put the 70D on it and let everything turned on.

Now, my philosophy about too big or too little. It's far more expensive to run too small a unit, overheat it too many times, and have it burn out when you need it most. That's what happens to many little gas units around here. Most sucumb to failure on the electrical side, and not the engine side. Lots of go carts around here running ex-generator engines.

The little bit of extra fuel cost is negligible IMHO, when compared to how much cooler my 25KW unit is when running at only 8 or 10 KW. Also, the larger armature and inertial mass of this 1800 rpm large unit, smoothes out the power pulses when using the 70D on it. Of course, my choice in size was also predicated on the deal that I got, so bigger was much, much better in my case. I could get by on less, but it sure makes for fewer decisions at a critical times like emergencies.

I use a Kill-O-Watt meter at the generator, and another in the kitchen so I can monitor it when I set the throttle, and from the house as well. I bought an oil pressure cut out "Murphy" switch (used on Thermo King units) to protect the 4310 in the event of an oil pressure loss. It's a handy idea even during regular times. It ought to be standard equipment on tractor engines.