My family and I are presently "house sitting" for part of the winter. The house we-re in is 15 years old and I've got some questions about the heating system. It has a propane fueled boiler. Half the house is on baseboard and the other half has "radiant" heat with plastic pipe in the floors. Some furnace repair guys were here just before we arrived a few weeks ago and supposedly "tuned it up." Well - none of the radiant heat works at all. The baseboard works fine. Since this house is super-insulated - it still stays pretty warm even with only 1/2 the heat working and it being 8-12 degrees F outside.
I'm trying to diagnose best I can and would like a general idea of how this sort of system is supposed to work. I'm not clueless with low-tech heating - but this thing is complicated. There are wires running all over the house and there are no plans or schematics.
The Weil-Mclain boiler makes all the heat and domestic hot water. The baseboard heat works fine but I see no circulator. Maybe hidden somewhere? Doesn't matter I guess.
The radiant system has mostly Wirsbo components. Has a circulator, a relay, and a big manifold with a series of "telestats" or "actuators."
When a thermostat is turned on to make heat - the actuator hooked to it will respond and open. But - the circulator does not come on so there is no heat. I can run a jumper wire across two low voltage terminals on the circulator relay and then the heat works.
So - I'm hoping someone here can tell me generally - how this system is supposed to work. I went to the Wirsbo Website and read a few of their manuals. Problem is - there manuals all show the use of a circuit board called a "Zone Control Module" that acts as an interface between the thermostats and actuators. This house has none. Maybe the older systems did not have them?
I'd like to know what order of things happen when a thermostat calls for heat in this system? It opens an actuator in the hot-water manifold. But - what sends a signal to the circulator? Any help appreciated. I may have to trace every wire and draw a schematic to get an understanding of this mess.
I'm trying to diagnose best I can and would like a general idea of how this sort of system is supposed to work. I'm not clueless with low-tech heating - but this thing is complicated. There are wires running all over the house and there are no plans or schematics.
The Weil-Mclain boiler makes all the heat and domestic hot water. The baseboard heat works fine but I see no circulator. Maybe hidden somewhere? Doesn't matter I guess.
The radiant system has mostly Wirsbo components. Has a circulator, a relay, and a big manifold with a series of "telestats" or "actuators."
When a thermostat is turned on to make heat - the actuator hooked to it will respond and open. But - the circulator does not come on so there is no heat. I can run a jumper wire across two low voltage terminals on the circulator relay and then the heat works.
So - I'm hoping someone here can tell me generally - how this system is supposed to work. I went to the Wirsbo Website and read a few of their manuals. Problem is - there manuals all show the use of a circuit board called a "Zone Control Module" that acts as an interface between the thermostats and actuators. This house has none. Maybe the older systems did not have them?
I'd like to know what order of things happen when a thermostat calls for heat in this system? It opens an actuator in the hot-water manifold. But - what sends a signal to the circulator? Any help appreciated. I may have to trace every wire and draw a schematic to get an understanding of this mess.